Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Quick Response Sprinkler requirement

Status
Not open for further replies.

cb1151

Mechanical
Joined
Jan 27, 2006
Messages
12
Location
US
Can someone PLEASE help me out here. I know in the past I've seen a clear ruling in NFPA 13 showing that quick response sprinklers are required for new construction but I can't seem to find it. The only thing I can find is under thermal sensitivity but that states for light hazard. My application is Ordinary Hazard.

Anyone know what I'm referring to? I knew I should have tagged it when I found it the first time! DOH
 
Isn't it strange that they only have a requirement for light hazard? I must be thinking of something else but I thought there was something stating it other than 8.3.3.1.

This is for a preaction system if that helps any?
 
QR Sprinklers are only required for light hazard occupancy. The big advantage to using QR sprinklers in an ordinary hazard occupancy is that you can reduce your remote area size, however you have a pre-action (dry) system so you are going to be calculating 1950 square feet no matter what.

At this point it's a matter of economics and since hydraulically their is no advantage to using the QR sprinklers (can't reduce the remote area) you can save a few bucks a head and using standard response.

 
I could have sworn I've seen something in a code that says light and ordinary but it must have been one of those many nights I'm having nightmares about work! Don't lie, it's happened to you too ;)

Thanks for all the input!
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top