Things are getting confused between different pieces of equipment.
The majority of electric motors are less than 100 HP.
These motors are typically controlled by manual motor starters or by magnetic motor starters.
There are two basic control schemes used with magnetic motor starters, two wire control and three wire control.
In both types, the overload relay contacts are
normally closed and open on an overload.
Some overload relays must be reset manually, Some will reset automatically. Some may be arranged to reset either automatically or manually.
Two wire control will restart automatically after a power outage.
Three wire control must be restarted manually after a power outage.
In both schemes, the overload relay contacts are always
normally closed.
Larger motors may be controlled by Air Circuit Breakers or stored energy breakers.
These are tripped by:
Removing current from a continuously energized low voltage trip coil by normally closed contacts on the protection relay.
or
Applying current to a shunt trip coil from normally open contacts on the protection relay.
In the case of the shunt trip there must be power available to trip the breaker.
This may be an additional point of failure.
In the event of a failure of control power the breaker may not be tripped remotely or automatically.
It may only be tripped off manually without control power.
OP said:
where is in normal feeder protection the relay contact is programmed as normally open?
Generally you do not want your feeder breakers to trip off when the power fails.
In many instances you do want your motors to remain stopped after a power failure. Safety is not the only reason.
Your system may not withstand the surge of restarting all of the large motors simultaneously.
Some machines must have the motors restarted in sequence. eg: The oil ump must bring the oil pressure up before the large motor is started.
Loaded conveyors must be unloaded in sequence before restarting, etc.
In these cases use a scheme that will trip the breaker on failure of power. Normally closed relay contacts may be the easiest way to do this.
You may use a normally open contact scheme if you have an alternate source of power for tripping.
This may be storage batteries, a capacitive trip unit or a UPS.
Bill
--------------------