I am presently looking at doing a Tier 1 or 2 analysis on an existing Tilt-up warehouse built circa 1983.
Problem is that the building is being converted from a warehouse occupancy to a school. If the occupancy is over 250, then the category goes from II to III, and the importance factor to 1.25 from 1.00.
The question is that I have found no mention of any importance factor in ASCE 31-03, and to properly anlyze the structure for it's intended use, in my mind, this should be included. Am I missing something here?
The obvious answer is that I could just include it in the gross shear analysis, but that would be too easy...
Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
Problem is that the building is being converted from a warehouse occupancy to a school. If the occupancy is over 250, then the category goes from II to III, and the importance factor to 1.25 from 1.00.
The question is that I have found no mention of any importance factor in ASCE 31-03, and to properly anlyze the structure for it's intended use, in my mind, this should be included. Am I missing something here?
The obvious answer is that I could just include it in the gross shear analysis, but that would be too easy...