I noticed that in the 2014 edition (and onwards to the current 2018 edition) of ASME B31.3 Section 345.4.2, the following clause was added regarding ST/S factors:
For reference here is parts a and b of 345.4.2 Link
I'm wondering what the motivation for using the minimum calculated ratio is. To me this is saying, if I have a pipe that has an ST/S ratio of say, 2, my test pressure must exceed 1.5(P)(2), however if I replace half of this section with some other material that happen to only a ST/S ratio of say, 1.9 (it de-rates slower with temperature), by this clause I can lower the test pressure of the entire system to 1.5(P)(1.9), which is less than the minimum hydrotest pressure required for the part of the component that de-rates faster with temperature?
"c) in those cases where the piping system may not include pipe itself, any other component in the piping system, other than pipe-supporting elements and bolting, may be used to determine the ST/S ratio based on the applicable allowable stresses obtained from Table A-1 or Table A-1M. In those cases where the piping system may be made up of equivalent lengths of more than one material, the ST/S ratio shall be based on the minimum calculated ratio of the included materials."For reference here is parts a and b of 345.4.2 Link
I'm wondering what the motivation for using the minimum calculated ratio is. To me this is saying, if I have a pipe that has an ST/S ratio of say, 2, my test pressure must exceed 1.5(P)(2), however if I replace half of this section with some other material that happen to only a ST/S ratio of say, 1.9 (it de-rates slower with temperature), by this clause I can lower the test pressure of the entire system to 1.5(P)(1.9), which is less than the minimum hydrotest pressure required for the part of the component that de-rates faster with temperature?