There are 2 negatives with using an oversized boiler:
1) Less efficiency. It is better to use a boiler running near 100% rather than one that cycles off and on. This is partly because there is a purge air cycle (required by law) at the start and end of every combustion cycle. I.e., the blower purges ambient air through the system and out the stack, wasting heat. I think about a 30 second purge at the start and end is required for a 1.5 Million BTU/hr boiler.
Boilers that operate at various turndown ratios (25, 50 & 75% for a small boiler) are better than cycling on and off, but you still have greater thermal mass and surface area to lose heat from, plus your boiler must be certified to meet the emissions limit at each firing ratio.
2) Air pollution regulations are more stringent for larger boilers, both the NO
x and CO limits and the frequency of testing. I have dealt with both Ajax and Rite, and both can supply boilers rated at say 990,000 BTU/hr to avoid the step up in regs at 1 Million BTU/hr. You need to talk to the right people, or maybe a vendor of multiple brands, e.g., R.F. MacDonald Co.:
The South Coast AQMD regulations are on-line at
Even if you are outside the SCAQMD, the other California APCD’s typically adopt the SCAQMD rules after a year or so (at least, Ventura & Santa Barbara do). Make sure to buy a boiler/burner combination factory pre-certified to meet the SCAQMD regulations (other districts will accept SCAQMD certs).
Our company recently had a Rite boiler overhauled, and we had it derated to < 1 Million BTU/hr. Estimated savings in fuel and testing > $2500/year.
Hope this helps,
Ken