That depends on how is the system designed. If you have one pump with a system curve joint at close to the Best Efficiency Point, and you add the second pump in parallel without modifying the piping system (except for the piping around the pump), the combined pump curve will join the system curve at left side of the BEP with lower efficiency. That means, the pumps consume more power than the increase in flow delivery.
If you added the second pump while modifying the piping system (with larger pipe size)to make the total friction lose same as previous for one pump, you are getting doubled flow with same efficiecy - just like as if you added a parallel system.