pump vault constr jts

Status
Not open for further replies.

profplan

Structural
Oct 16, 2008
46
I am reviewing the construction of a 60 ft x 12 ft x 10 ft deep concrete trench or vault for pumps in a wastewater pump building. The walls and base are 14" thick, reinforced with 2 layers of reinforcing, and sized to resist flotation from a high water table.

The design does not need to satisfy ACI 350 for liquid containing structures, but, excessive cracks or seepage would be objectionable.

Would you recommend any construction joints in the walls? Or in the slab? Waterstops are provided continuously in the walls at the base slab.

Thanks.
 
Replies continue below

Recommended for you

I would advise putting in one construction joint smack dab in the middle of each long wall. It should continue into the slab.
 
JedClampett,

Thanks. I thought over 30 to 40ft might require CJ's.
 