Those values are typical values that I've seen when dealing with fluids close to their boiling point. Basically, low velocity = low suction line losses that serve to minimize NPSHA issues.
On fluids where the temperature, pressure or elevation are such that NPSHA isn't as much of an issue, I've seen much higher velocities used. I did some work on a tank farm and was surprised at the suction velocities the inline pumps operated at (diesel, kerosene) coming off atmospheric storage tanks. If you are interested I can dig up the data but if memory serves me right, they were in the area of 10 ft/sec. The reliability of the pumps was very good I remember.
For example, if you are dealing with a cooling water booster pump where the suction pressure is say 30 psig, you have close to 100 feet NPHSA. In that case, I wouldn't use those values.