Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Pump Selection Questions

Status
Not open for further replies.

psugreen

Mechanical
Joined
Jan 29, 2008
Messages
14
Location
US
2 questions in relation to pump selection:

1. For inline pumps should suction and discharge connections be line size, or is it ok for the pump to have a smaller connection than the pipes it connects too?

2. What is the best speed (rpm) to select pumps at?
 
You can have smaller pump connection. Just use reducers properly, to avoid air pockets.

Nothing like the best speed. High speed pumps are smaller in size but life is shorter.

 
I usually try to select a pump with a four pole motor; 1500 or 1800 rpm.
 
Most pumps have a smaller outlet size than inlet, and both are usually smaller than the piping. As for speed, 1800 rpm seems to be a standard in most HVAC applications, however if you have high head and low flow, the 3600 rpm option will give a much more economical pump and also more efficient. Also, most condensate and booster pumps buck the trend and are 3600 rpm. Finally, some engineers specify 1150 rpm motors as they are assumed to provide a quieter system

Joe Lambert
 
Higher rpm pumps make more noise.

Pump inlet and outlet sizes are almost always smaller than the pipe in which it's mounted for a lot of reasons.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top