vinhermes
Marine/Ocean
- Aug 29, 2009
- 36
Dear All,
Small brain cramp today... This will seem obvious to many of you but it is not clear for me.
So, the components to determine the pump required pressure (for a given flow rate) is:
- static head
- friction (pipe & fitting)
- velocity head (ignored on my case)
But do I need to add the required pressure at the outlet of the discharge pipe? For instance, if this is a fire hydrant and that I want the water to flow at a pressure of say 5 barg, shall I add 5 barg to the pump pressure required by friction and head?
It seems logical but then I am afraid that the pump will only incease the flow rate to match its curve (for a pressure only equal to head + friction, without the 5 barg).
Hope I am clear enough (hard to explain clearly sompething while being confused). Thanks by advance, Vincent
Small brain cramp today... This will seem obvious to many of you but it is not clear for me.
So, the components to determine the pump required pressure (for a given flow rate) is:
- static head
- friction (pipe & fitting)
- velocity head (ignored on my case)
But do I need to add the required pressure at the outlet of the discharge pipe? For instance, if this is a fire hydrant and that I want the water to flow at a pressure of say 5 barg, shall I add 5 barg to the pump pressure required by friction and head?
It seems logical but then I am afraid that the pump will only incease the flow rate to match its curve (for a pressure only equal to head + friction, without the 5 barg).
Hope I am clear enough (hard to explain clearly sompething while being confused). Thanks by advance, Vincent