itsmoked
Electrical
- Feb 18, 2005
- 19,114
I have a thread over in "Pumps".
thread407-280636
To sum it up there is a pump down a hole that has a 10hp motor on it.
The load is about exactly 10hp.
The power is open delta. Two transformers mounted on a pole directly next to this well are running ONLY this pump.
The voltage at the motor starter is 242V between all legs.
The wire is number 6AWG running about 50 feet.
The motor, (a 10hp Hitachi), has an FLA of 29A.
Here's the problem: The currents are running at 31A, 31A and 34.5A...
Scotty has posited that the motor is probably a 230V expecting a 10V drop down a bunch of 'just big enough' cable. In this case the motor is likely having about 241V at its terminals.
Could we be seeing some saturation adding these extra amps?
The other question is why this nasty current imbalance? Could this brand new motor be bad?
Keith Cress
kcress -
thread407-280636
To sum it up there is a pump down a hole that has a 10hp motor on it.
The load is about exactly 10hp.
The power is open delta. Two transformers mounted on a pole directly next to this well are running ONLY this pump.
The voltage at the motor starter is 242V between all legs.
The wire is number 6AWG running about 50 feet.
The motor, (a 10hp Hitachi), has an FLA of 29A.
Here's the problem: The currents are running at 31A, 31A and 34.5A...
Scotty has posited that the motor is probably a 230V expecting a 10V drop down a bunch of 'just big enough' cable. In this case the motor is likely having about 241V at its terminals.
Could we be seeing some saturation adding these extra amps?
The other question is why this nasty current imbalance? Could this brand new motor be bad?
Keith Cress