rafcu,
In most of the SIL 2 applications that I have seen, the required solution is typically 1 (usually SIL 2 rated/cert) or 2 transmitters (SIL 2 rated/cert or not). I have not seen a SIL 2 application where the required solution is 3 transmitters. I guess yours is the first for me. As such, I don't have any experience with replacing 3 transmitters with a single SIL2 certified transmitters. Again, "Does your customer's safety standards require 2oo3 for SIL2? If so, then you still need two PTs."
With respect to John's post, I would like to add that, usually, each transmitter's signal (any sensing signal for that matter), goes to a single input channel in the safety system. It us unusual for a single sensor to go to multiple channel in a safety system. There are several reason.
One reason is that it is best to keep the safety system simple and clear - and one-to-one is simple and clear.
Also, another reason is that usually, the weak link is the sensor (including element, transmitter, wiring, all), and not the safety system (I/O module, back plane, inter-connections, processor, power, all). In fact, the safety system is usually the strongest link in the safety chain.
The strength in the safety chain, in decending order of strength, is usually:
1) safety system
2) sensing element
3) final element (valves)
Please note "usually", as there are exceptions.