OP said:
The class society guy wants us to prove the integrity of reverse power relays as part of his intermediate (2.5yr) survey. He suggested other operators choose to actually induce a real reverse power situation by taking load off one set and driving the set frequency up on the other so as to motor the unloaded generator.
Do you want to comply with this, or argue.
Consider:
When you are at sea and a prime mover fails for some reason and the reverse power relay operates, what will happen?
If you are not operating on an N + 1 basis things may get interesting.
If a set fails and you must depend on the reverse power protection to take it off-line the system frequency will stay the same or drop a little.
Function testing is simulating real world conditions.
eg: a set has failed for some reason.
You can simulate this by cutting the fuel or steam to the set under test. This will not only test the reverse power protection but will also show the ability of the system to recover from a reverse power event on one set.
QUESTION:
Do you want to get a box checked and signed on a report form or do you want to be assured that the the system will provide stable continuing power in the event of a set failure while at sea?
Different types of prime mover have different negative reactions to reverse power. That is why we use reverse power protection.
Your best function test is to induce reverse power and let the reverse power protection operate. This may also be the quickest and safest.
You can induce reverse power quickly by cutting the fuel or induce reverse power smoothly by setting the speed slower.
If you do not use an N + 1 scheme an induced reverse power test may give you some preview of what to expect when a set fails at sea at 2:30 A.M.
Bill
--------------------