Ravenclau
Agricultural
- Aug 10, 2020
- 4
Hello everyone,,
In a scenario where the breaker rating is lower than cable ampacity that the breaker is protecting, isn't the overload protection automatically applied by the virtue of the CB rating being lower than the cable ampacity? For example, 100A mains protecting 1/0 service conductors. If the breaker is equipped with thermal magnetic overload or long time delay function, it will eventually trip before the allowed amperage of the 1/0 cable is exceeded.
Am I right on this? I could see a scenario where a 30 Amp breaker is protecting a #10 conductor, you'd not want to use MCP, you'd need a long time delay element on the breaker.
Thank you for your feedback.
God Bless.
In a scenario where the breaker rating is lower than cable ampacity that the breaker is protecting, isn't the overload protection automatically applied by the virtue of the CB rating being lower than the cable ampacity? For example, 100A mains protecting 1/0 service conductors. If the breaker is equipped with thermal magnetic overload or long time delay function, it will eventually trip before the allowed amperage of the 1/0 cable is exceeded.
Am I right on this? I could see a scenario where a 30 Amp breaker is protecting a #10 conductor, you'd not want to use MCP, you'd need a long time delay element on the breaker.
Thank you for your feedback.
God Bless.