I have seen Japanese also including the ammeter in the secondary ckt of protection class CT.
I think it is no problem considering that present day meters can withstand 10times the rated current for 0.5second, typically.
The protection class CTs are mostly with accuracy limit factor 10 (say 5P10 to IEC).