I will add another feature of the SEL relays that I find very useful in commissioning and relay testing.
SEL calls it a "Relay Word Bit". It is a logical element in the relay (an input (IN101), an ouput (Out101, TRip, 51PT, 32QF, etc). If the relay word bit is listed in the book, this can be displayed logically (show me this bit "n" times in the terminal display), or freely mapped to a contact output, or displayed via an LED.
Testing procedures for EM relays often called for blocking a contact open or closed (with a $20 bill to remember to remove). A SEL relay can be programmed to act a same way (via an unused output contact (Testing)), to either replicate existing testing standards / procedures, or for troubleshooting & commissioning, keeping the main tripping contact logic intact. This is extremely useful when trying to get ones head around the logic of both the relay algorithm and the settings applied. I have found that for both expediency and clarity, being able to "see" what the relay sees is very useful.
One further note about SEL relays and instruction books. In the SEL 251 series instruction manuals, there is an application note on how using both a bus and feeder arrangement of relays (via different setting group selections), a bus and feeders can be protected for a failure of a feeder relay (via 2 sets of self fail alarm contacts), can tell the bus back up relay there is a failure (change settings and become more sensitive) and via Aux relays and wiring (no more complicated than a lock out relay scheme), to trip the feeder (and only that feeder) that has a failed relay. With additional wiring to this scheme (a "Feeder Relay in Test Mode" Switch, this also allows for feeder relay testing / maintenance while still providing adequate protection with the feeder in service. I commissioned one of these schemes, as outlined in the SEL 251 manual when I was still a greenhorn. Years, later I see the beauty of this as it also allows the maintenance of a feeder relay in service. This scheme could be applied to any digital relay with proper design (and 2 alarm outputs).
As has been mentioned earlier, if one has not been exposed to a SEL relay, it can at first seem intimidating. When written out, it is an Algebraic math argument (TR = 51PT +(OR) 51GT *! (AND NOT) 50L). Algebraic order of operation matters.
I've seen the GE Brick system and challenged a qualified GE applications engineer to really show me how it works. It does and the hardware for the brick (ADC - 61850) is very robust, the fiber patch system is logical, etc. GR UR series relays do have some very compelling features. I think with a brick type solution, for example, it would be possible to add 87B (Bus Diff) to nearly any circuit and that would help to solve the arc flash problems for many.
At least here in the USA, there is still a reluctance to take that next step. One reason may be that when a mis-operation occurs, there is hell to pay for the folks in the field (and others Im sure). With current technology (non 61850), we have test and isolation switches that are (hopefully) available to make checks for trip signals, volts, amps, etc. On a new project where everything could be tested via primary injection, confidence could be gained. On upgrade/brownfield projects, where it is a 40+ year old station (with old, unreliable drawings) this could be a problem. If, for example we already have issues with settings and drawings now, how about with a non standard implementation of 61850 that was not well documented ( in the field) 40 years from now.
Watt and Var consumption (mostly real power) has occured