Proper thermometer installation

Status
Not open for further replies.

Kevinj12

Mechanical
Mar 24, 2007
1
I am looking to install thermometers in a radiant heating system. I want to install them into the run of the supply and return on large loops and was wondering if the whole stem of the thermometer should sit in the entire way or is just the tip ok. 3/4 copper tubing and the thermometer has a stem that is 5/16 in dia. Any help would be great.

Thanks in advance
 
Replies continue below

Recommended for you

Generally with these dial type thermometers you need a thermowell. The thermometer device just inserts into the well and has a spring clip or thread to hold it tight to the ID of the well wall.

Uponor Wirsbo offers a nice (cheap) little dial-type thermometer which comes with a little brass well with a metric thread and o-ring- probably a G 1/4. It's designed for use with their (expensive) manifold fittings. I just bought 3/4 x 1/2" solder socket tees for each thermometer location (nominal size copper water "pipe" (i.e. 1/2" nominal "pipe" is actually 5/8" OD), threaded the ID of the 1/2" branch using a 1/4" NPT tap, threaded in the well and SOLDERED the threaded joint to seal it. Seals perfectly and works well.

If you're looking for radiant heating advice, a better forum than this one is "the Wall" at
 