Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Propane gas and electrical enclosures.

Status
Not open for further replies.

sloop

Mechanical
Joined
Apr 18, 2003
Messages
7
Location
US
I have a project where the LP gas manifold is inside the electrical panel enclosure. Is this appropriate? It has been suggested that I could build a shield inside the enclosure to seperate the electrical and the Gas.
 
I think this is more of a standard issue and not NEC. The requiremnts is that all fluids be located in a separate enclosure away from electrical componets (AC or DC). The exception is that if an electrical device is directly a part of the Valve, solenoid or regulator controlling the Fluid it is acceptable to be in the same enclosure.

So your right, Gas is considered a fluid,it is not allowed. As a matter of fact pneumatics are considered a fluid and also are not allowed. Your other issue is if the LP gas is volital, all the electricals if located in the same enclosure would have to be rated for explosive atmosphere and the enclsure would have to be rated for explosive atmosphere. This would be big big money to design an enclosure for that type of application.

Christopher Caserta
ccaserta@us.tuv.com
Ph:904-225-0360
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top