MattJM
Structural
- Aug 28, 2007
- 28
Can anyone shed light on the use of the factor used in the UFC (as follows) for enhanced local resistanc of columns?
The purpose is to guard against shear failure below the flexural capacity of a column, so the provisions require that the column be designed for the shear resulting from uniform lateral load at the three-hinge formation condition in the column. For a pin(base)-fixed(top) column, the examples use
V = 7.5 * Mp/h,
where h is the column height. Not much explanation is given.
A lower factor can be derived for this condition (V=6.83*Mp/h).
Does anybody else have an explanation for the increased value? Is the extra 10 percent for any of the following reasons:
Column not actually pinned at base? (Fix-Fix has factor of 8)
Overstrength?
Something else I have probably missed?
Note: The progressive collapse seminar I attended way back also indicated the use of the 7.5 factor.
Thanks
The purpose is to guard against shear failure below the flexural capacity of a column, so the provisions require that the column be designed for the shear resulting from uniform lateral load at the three-hinge formation condition in the column. For a pin(base)-fixed(top) column, the examples use
V = 7.5 * Mp/h,
where h is the column height. Not much explanation is given.
A lower factor can be derived for this condition (V=6.83*Mp/h).
Does anybody else have an explanation for the increased value? Is the extra 10 percent for any of the following reasons:
Column not actually pinned at base? (Fix-Fix has factor of 8)
Overstrength?
Something else I have probably missed?
Note: The progressive collapse seminar I attended way back also indicated the use of the 7.5 factor.
Thanks