There is something stange about Case 2 firstly because our grid resistances are so far out ( published value = 5.5 ohms, myself=5.43 ohms, yourself=7.693 ohms). Based on such large differences, it isn't surprising our step and touch voltages are out. What is puzzling is, I think, based on what I know of the authors of the published paper, that you would be using the same software.
I note my greatest discrepancy lies in step voltage calculation while touch voltages are pretty close - Case 2 excepted. The program first calcuates the current in each of the grid elements. Then surface potentials are calculated at whatever spacing I want ( e.g. every 1m, .5 m, etc). From these values it is easy to calculate the touch voltage and step voltage by simple math operations ( i.e. subtraction) on the GPR and individual surface point voltages. Since my GPR's and touch voltages seem to line up pretty well with your results ( Case 2 excepted), I expect that my logic for calculating the element currents and surface potentials is acceptable. So why the larger errors in step voltage? I am thinking I may need to calculate surface potentials at a smaller increments.