I may be able to shed some light on it...
Down here in the Windsor area, it appears that the problem stems not from the pipe itself but rather a couple contractor's who installed it. Basically, it was installed in a similar manner to concrete pipe which requires only minimal compaction of the bedding and cover material to maintain its integrity. However, since PVC pipe, and Ribbed Pipe especially, requires proper compaction of the bedding and cover to provide pipe strength, the pipe failed. Now, this happened long ago and only a couple times, but it was enough to taint ribbed pipe in the minds of several of the local town engineers. Then the town engineers all get together and share horror stories... well, the "taint" just keeps spreading.
Just as a side note, I was able to use ribbed pipe in one of the "tainted" jurisdictions by enforcing the requirement for compaction testing of the bedding and cover material prior to backfilling. As this type of testing wasn't standard practice down here it raised the install price, but it still worked out cheaper in the end.
David Dietrich
KMK Consultants Ltd
Windsor, Ontario, Canada