jraef
"Also to be honest, I'm not interested in yanking information from you one little piece at a time."
people come to this forum seeking knowledge, answers to questions, and help with problems; not arrogance, which serves no one well.
--------------------------------------------------------------------------------
7182....With regard to the motor, voltage is
NOT the issue; volts/Hertz is.
At 220 - 50 ... that motor is designed to operate from a source that can supply
4.4 v/Hz ..... at 208 - 60 .... motor sees 3.4666 v/Hz ... and is underexcited by 13.33% (I've seen specified 208 v sources come in at a nominal 195 v, which further exacerbates the problem).
(At 4.4 v/Hz, as jraef stated, it would take a 264 v source at 60 Hz to achieve that v/Hz. Not only is that impractical, but it would create additional problems for the motor which would operate above its design parameters for speed, torque and Hp~kW)
The buck-boost solution previously proposed, while it addresses the voltage concern, does not address the
v/Hz issue which is the primary concern for the motor.
The additionl concern for the motor is one of speed-torque-Hp(kW).....
To eliminate the v/Hz dilema, consider:
[li]reconnect the motor for 380v[/li]
[li]obtain a 280/480v step-up transformer of the proper kVa rating... (a 480/208v step-down transformer could be used...and use the secondary winding as the primary ... and the primary winding as the secondary)[/li]
[li] obtain a 480v VFD (v/Hz... scalar.... type is all you'd need ... don't need vector unless there additional considerations of the application you haven't shared with us).[/li]
[li] set the MAX Output parameter(s) volts and freq.... for 380/50.
Note: if VFD doesn't have ability to limit max volts and frequency, then set the MAX SPEED parameter for the nameplate RPM of the motor.[/li]
That will take care of
only the motor issues.
Since we have no knowledge of the make-up of your control panel, we are unable to offer any advice for resolving how to make a European design find happiness in the USA/Canadian?? world.
You could, of course, begin a very necessary dialogue with the manufacturer (OEM) of the machine that you purchased; even if you are not their primary customer for this machine ...i.e., you purchased it from a 3rd or 4th party.
I somehow get the feeling that you tried to save a few $$$ by buying something second hand without understanding all of the ramifications. Unfortunately, its gonna cost you more in the long run to get it up and running. Perhaps an old expression: Penny Wise and Pound Foolish is or Lessons Learned the Hard Way .... is apropos ???
Good luck