Let me expatiate: For those who are not familiar with probe type low water cut offs... it is a simple relay circuit where the relay coil current passes through a probe extended into the boiler water and through the boiler water itself. The energized coil closes normally open contacts and completes the boiler interlock circuit. If the water level falls and no longer makes contact with the probe, the coil circuit is interrupted and the coil de-energized.
Since the boiler water is part of the current path, its resistance is a factor. Obviously if the resistance of the water was high enough to limit the coil current to something lower than the coil's minimum pull in current, the coil will not pull in or drop out if already energized.
To my case...
The boiler is a 30 hp firetube low pressure steam boiler. There is nothing unusual about it. I have of course checked the usual suspects: corroded probe, loose electrical connections, fluctuating water level.
As part of my troubleshooting, I wanted to simulate the probe/water part of the circuit using a potentiometer. To do this I need to know what pot value I need to use; 100K pot, 50 ohm pot, 10Meg pot, what? I thought this would be an easy thing to find. I'd find some reference stating that the normal resistance for boiler water in a low pressure steam boiler with average water treatment chemicals and TDS (total dissolved solids) is in the range of 100 ohm per inch or 2K ohm per inch.... at least a ball park guess but nothing.
I am now communicating with McDonnell & Miller who makes the control I am using and who should have the exact information I need. In the mean time I greatly appreciate the folks who have responded. Thanks