Mechanical
- Dec 10, 2007
- 11
I am investigating a low hot water flow issue for a single building served by a district heating plant. The pumping system is designed as a constant speed primary distribution with varible speed pumps serving the building loads. A three way mixing valve maintains the building loop temperature. The building loop is decoupled from the primary hot water system via an open flow path. The constant volume primary system is regulated with a balancing valve downstream of the decoupler/building return point of connection. This balancing valve maintains primary loop flow. However, during building use, it appears that the decoupler could have reverse flow even at flows less than system design. Since the balancing valve is downstream of the decoupler point of connection, if the pressure is higher in the building return than the supply line (possible with the pump energy added at the building), the flow is reversed. Is this a possible issue that I should study? My initial thought is that if the balancing valve was in the decoupler line, then this would essentially create the pressure drop that the system requires to work properly. Reverse flow would be less likely.
In reviewing the ASHRAE Systems and Equipment handbook, the balancing valves in Fig. 19 appear to be shown in the position that is currently installed in this building and not in the decoupler (common pipe). Is there a reason why it does not get installed in the decoupler?
Thank you.
In reviewing the ASHRAE Systems and Equipment handbook, the balancing valves in Fig. 19 appear to be shown in the position that is currently installed in this building and not in the decoupler (common pipe). Is there a reason why it does not get installed in the decoupler?
Thank you.