In addition to My experience over the past 30 years, it is the opinion of the ASME that Pipe size has something to do with PRV size. ASME Sec I, Power Boilers, requires the inlet and outlet piping be at least the the size of the PRV Connection.
This is a quote from a proposed new ASME Sec XI for Transport Tanks, "TR-130 INSTALLATION REQUIREMENTS
(b) All piping, between the pressure relief device and the vapor space of the tank, shall not be less than the size of the pressure relief device inlet to ensure that flow capacity is not compromised. When two or more required pressure relief devices are connected to a single opening, the internal cross sectional area of the opening shall not be less than the combined inlet areas of the pressure relief devices connected to it.
Both Farris Engineering and Dresser Consolidated Troubleshooting Charts refer to Undersized Inlet Piping as a major cause of Chatter. A quote from Crosby, "A valve should never be installed on a fitting having a smaller inside diameter than the inlet connection of the valve."
According to API RP576, 5.2.c., "Improper or lengthy piping to the PRV inlet…can cause a PRV to chatter. The pressure under the seat may become great enough to open the PRV. However, as soon as the flow is established, the built-up pressure drop in the connecting piping may be so great that the pressure under the seat falls and allows the valve to close. A cycle of opening and closing may develop, become rapid, and subject the PRV Seating Surfaces to severe hammering, which damages the seating surfaces, sometimes beyond repair."
Regarding Built-Up Back Pressure in the Outlet Piping,
Farris Engineering Manual 192-T states the following:
Problem: Chatter.
Cause: The outlet piping is of excessive length or the diameter is less than the valve flange size.
Corrective Action: Design outlet piping so that pressure on the outlet does not build up causing the valve to shut.
Consolidated Maintenance Manual CON-2 states:
Problem: Chatter.
Cause: Built-up Back Pressure
Corrective Action: Check outlet piping
BobPE you acknowledge Oversizing as a cause for chatter.
If you think about it logically, reducing the inlet piping or making it excessively long both have the same effect on the operation of a PRV as placing a large, high capacity PRV in a low volume application (oversizing). Basically there is insufficient volume to maintain the reaction force in the PRV Huddling Chamber necessary to overcome spring force.
J. Alton Cox
President
DeLuca Test Equipment