Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations LittleInch on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Pressure Testing Water Main with Super Chlorinated Water

Status
Not open for further replies.

coloeng

Civil/Environmental
Joined
Apr 1, 2008
Messages
345
Location
US
Anyone know of any drawbacks to pressure testing a new C900 PVC main while the super chlorinated water is in the line?
 
If you are pumping the system up to the hydrostatic test pressure, you would have to use disinfected water. Your pumping test equipment would also have to be disinfected.
 
I would also think there may be the catastrophe scenario where if a valve or flange let go during testing you would have to explain why you dumped many gallons of highly chlorinated water into the environment. On the flip side, you might be able to smell any leaks as well as see them!
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top