15 bar is not working pressure for chilled water loop for sure (meaning i could bet) and very few usual equipment pieces will sustain 22 bar testing pressure. these are not hvac pressures.
10 bar can be working pressure for water supply or fire extinguishing systems, and than 15 bar can be testing pressure, but not for circulating systems.
can you give us some example of equipment - fan coils, heat exchangers or similar attached to your chilled water loop?