...I'm still a bit uncertain on how to determine pressure on basement walls.
It's a gray area of design, and there isn't a lot of good research on the subject. You have to apply a lot of judgment.
Can I use an Equivalent Fluid Pressure? AND, treat it like hydrostatic pressure?
Yes, provided you understand the limitations of the approach. In general, the use of an Equivalent Fluid Pressure works best when a wall is cantilevered i.e. has no bracing or restraint above the bottom of the wall. If the wall is braced or restrained, a trapezoidal pressure distribution (Peck 1969 "State of the Art" paper presented at the ICSMFE in Mexico City) is more appropriate. Peck's pressure distribution starts at zero at the ground surface, increasing to 0.3 to 0.5*&[ignore]gamma[/ignore];*H at the level of the top brace or restraint; the pressure remains constant to the bottom restraint or brace, then decreases to zero at the bottom of the excavation (if the section of wall below the bottom restraint is "free"
. The factor H is the total height of the wall; &[ignore]gamma[/ignore]; is the total unit weight ("density"
of the soil; and the 0.3 to 0.5 factor is chosen based on how long the wall will remain in service (with a higher factor for longer service.)
It wasn't intended for permanent walls, but generally gives a somewhat more conservative (and, in my view, realistic) view of the earth pressure magnitude and distribution. When in doubt, analyze the wall both ways, and take the more conservative answer.
Is this an acceptable practice?
The answer depends on what has become locally accepted practice; but generally the answer is 'Yes.'
Should I be using a Factor as it appears this author did?
Yes. The factor will depend on the design method, of course - it may or may not be applied directly to the earth pressure values.
I thought figuring earth pressures on basement walls (retaining walls) would be easier than it is proving to be.
Perhaps you are beginning to understand why many geotechnical engineers consider their sub-discipline as more art than science -
Thanks again
You're welcome!
Please see FAQ731-376 by [blue]
VPL[/blue] for tips on how to make the best use of Eng-Tips Fora.