Are you sure the stat branch line builds pressure on a call for heat. Normally the opposite is true. The branch line exhausts to drive the VAV controller to close to minimum for reheat airflow(The VAV controller will have a seperate supply main).
To verify the stat:
Start at the stat-is supply pressure sufficient to close the switches, if not problem is in the pneumatic supply not the stat.
Next check the stat output-disconnect the branch and connect an accurate gage. Turn setpoint to full cooling(on DA stat temp up pressure up)- gage should read supply pressure.
Next,if not, depends on the type of stat but most brands have replaceable arms. Old school actually... today most would just try a new stat.
If yes then verify tubing to VAV controller. Disconnect branch line at controller and repeat above steps....
Enough steps for now, Reply with how you make out.