Pressure Guages at Suction

Status
Not open for further replies.

jrrocks

Mechanical
Aug 13, 2018
58
In closed loop chilled water pump system, my discharge side pressure gauge shows 30m (3kg/cm2) and suction side pressure gauge shows 5m (0.5 kg/cm2). To calculate the power of my pump which is 70% efficient, head should be consider only for discharge i.e. 30m OR should I consider 35m (30m discharge + 5m suction) OR 25m (30m-5m)?


 
Replies continue below

Recommended for you

It's differential head that the pump is supplying to the system so in your case here it is 25m.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
 
Agreed, diff head would be 25m if both suction and discharge PG readings are in kg/cm2 guage.
 