I have just completed a university project. Air balancing contractor is coming back with excessive resistance on REF1.
REF1 is a booster behind the mixing box on 30ton air handler. REF1 is rated for 11,000 cfm. On each side of REF1 I have and Industrial accoustics 5ES silencer 42x36-60 with a face velocity of 1000fpm and a static pressure drop of .24
The ductwork is the same size as the silencers so I cant see how this is correct or why they are not a little bigger to allow less static given the fact that there is 1 each side of the fan
AIr balance contactor states that of the 11,000 we are only getting about half that at the air hadler. Can anyone do a quick calculation on this to see if a mistake was made on the plans? system design is .75 TSP @ 11,000cfm current reading is 5,340cfm .73 TSP