Prequalified Moment Frame Weak Axis Single Sided Cruciform

Status
Not open for further replies.

calpolyjdg

Structural
Dec 23, 2008
1
I've run into a question that I could use all of your help on. Do you know if there is any testing or documentation specifically allowing (or not allowing) a weak-axis special moment frame (RBS) connection to a WF column with only a cruciform on one side (only a WT on the side of the moment frame connection instead of WTs on both sides).

Thanks for your help.
 
Replies continue below

Recommended for you

Judging by the extent of effort required to create the ANSI/AISC 358-05 along with the extremely specific nature, I would guess no is the answer. If for example you have a SMF, I believe you do have the option of demonstrating that your connection (designed accordingly) can withstand the deformation and strength requirements of the ANSI/AISC 341-05. My guess is it will be very difficult to do with the shapes you are proposing.
 