I assume these are tappered portal frames... Do you have the original drawings? How much information are you able to obtain? Depending on how familiar you are with cold-formed steel and buildings using same for bracing, etc, you may want to read "Bracing Cold-Formed Steel Structures" by Thomas Sputo & Jennifer L. Turner.
Remember: Tappered columns and rafters are meant to match the required capacity at given locations and generally result in economies when material costs outweigh labour. If you consider the bases pinned, and reverse engineer the bending capacity of the sections at the knee, you can work out the lateral load capacity for the three "old fasioned" cases (ie: wind against both walls, wind on one half of roof, and wind on full roof). The UDLs in each case that produce the knee BM (be careful to check mid-span rafter BM as well) will give you your capacity.
You may also wish to include a nominal fixity at the base (perhaps 10% of EI as a maximum). Moment redistribution is also possible, but you did ask for simple, right?
Let me know if you don't have tables of portal frame analysis formulae, I can scan and post if need be.
Good luck,
YS
B.Eng (Carleton)
Working in New Zealand, thinking of my snow covered home...