Question about rho_L and rho_t, which is the transverse and longitudinal reinforcement ratios in shear walls.

1743550345512.png

We are talking about horizontal distributed reinforcement versus longitudinal.

There is some discussion about which bars are which in regards to these ratios, especially since precast walls are a different animal. Some folks argue that longitudinal is in the longitudinal axis of the individual precast member, while others (myself included) argue that it is the longitudinal axis of the precast stack of panels (e.g. the 75' panel stack).

This is somewhat pointed out in the code.

1743550504253.png

hw/lw points to the type of failures between 'squat walls' and typical shear walls (flexural walls?).

In the equations, as hw/lw increases and approaches 2.5 we approach 0.0025 as the minimum longitudinal. As that ratio gets smaller it become a 'squat wall'.
The commentary says that horizontal reinforcement is less effective than vertical in squat walls.

In my mind, its because the 45 degree shear plane in a squat wall is oriented more horizontally and you'll get more benefit from vertical than horizontal.

1743550695084.png
1743550713549.png
Really, a simple diagram in the code book would clear this all up. (Any code book writers out there?)

Anyway, I feel like I've seen a diagram on this site describing the different failure mechanism between squat walls and the others.

But in any case, can someone clear this up?
 
Squat walls crack as you've shown, but very skinny walls—whether concrete or masonry—behave more flexurally wherein cracks originate near-midheight and propagate horizontally. It follows that up-down (i.e., vertically oriented reinforcement) is important for flexure-dominated walls.

Below is a complete guess, as I don't do much precast, so feel free to ignore.

From ACI 318-19(22):
1743594752140.png
1743594789300.png
1743594629342.png
1743594766363.png
1743594985041.png
1743595002235.png

Note the change from hw/lw to hw/rohw. Also, 11.6.2 gives it away:
1743595317980.png
1743595334470.png

So, because we're primarily interested in lateral shear strength, roht is for horizontally oriented (or "left-right," in elevation) reinforcement. Structurepoint supports this interpretation. If I'm wrong, then someone will rush to correct me, so we all benefit.
 