Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Precast panel=Reinforcement palced centrally in panel or at top & btm?

Status
Not open for further replies.

tngv752

Structural
Joined
Sep 16, 2004
Messages
91
Location
AU
In precast Panel or concrete panel for lift shaft, reinforcement is normally placed centrally or at the top and bottom of the panel ??

Thkx.
 
How thick is your panel?

Depends also on whether loads are applied from one side only or from both sides.
 
With precast, your loads are applied from both sides. Negative moment on the face of the panel during stripping, both positive and negative moments on the face of the panel during wind pressure and wind suction, and don't forget shipping and handling. Try to push the architect for a thickness that will allow you to double reiforce the panel. You can do this by referencing the PCI manual. Typically with precast, specs. will require an uncracked section. We all know that reinforcement is useless unless the panel cracks, and with precast, cracking stress is lowered to 5*sqrt. fc'. Good luck.
 