Precast Ground Beams

Status
Not open for further replies.

engstructural

Structural
Jul 15, 2008
60
I was looking at an engineers design (UK) for precast ground beams supported on small poured insitu pilecaps. When the beams are placed the joints are poured.

Some of the beams had 3No. 32mm bars in the bottom (3 No. 12mm bars top)(straight) and they had approx. 150mm bearing on the edge of the pilecap. To anchor / tie the beams at the support was a single 12mm U bar.

Designing insitu foundations I would carry min. 50% of bottom steel to a min length of 12 Dia. passed the centre line of the support (centre of cap).

Is this precast system OK without either U or L bars at the end of the precast beams and only 1 No. 12mm U bar across the centre of the cap?
 
Replies continue below

Recommended for you

The development length is not sufficient by ACI, but different codes give different minimums.
 