bacon4life
Electrical
- Feb 4, 2004
- 1,531
In the attached waveform of a successful 115 kV circuit breaker reclose, what accounts for the 2 cycles of current before the inrush from time 1.3 to 1.347? During this time the digital fault recorder shows about 35 amps with no harmonics. At time 1.347, the current jumps to around 300 amps with significant harmonic distortion indicating transformer inrush. Prior to the fault, the PCB had about 50 amps of load.
This line only recloses from one end, which explains the difference increased load after reclosing. Previous reclose events captured by this DFR also show the same pattern. Unfortunately the relays are not set to create records of successful recloses.
This line only recloses from one end, which explains the difference increased load after reclosing. Previous reclose events captured by this DFR also show the same pattern. Unfortunately the relays are not set to create records of successful recloses.