I would like to input a few comments here:
JAE is correct in the snow load capacities, but this will only hinder your success if you are designing this building in the South (the biggest region of PEMB suppliers).
1)I would like to advise you to model the typical interior rigid frame in RISA 2D/3D, STAAD, or some other similar program. This can be done easily if you are familiar with the member size tables offered in the rigid frame profile page of the PEMB drawings.
2)Ask for the shop drawings from the PEMB, and if they aren't available primarily because of "Murphy's Law", then visit the site and visually inspect the welds and the endplates. It is very rare for a PEMB company to design moment connections that are not shopweld/field-bolted connections, so it may be necessary to upgrade the connections too.
3)If the steps of 1 and 2 don't help, it may be better to pass the buck to the PEMB. Unfortunately, because I've worked for a couple of PEMB's (no longer), they aren't always the most honest folks. They will tell you they can't find the calc's and then they will bend over backwards for you to sign a contract to retrofit their own building.
Regards,
OUe