bytebyte said:
... So the customer is being billed for kVA usage. From reading the replies, this powersave device can lower his utility bills by correcting his power factor; hence reducing his power consumption. This device wouldn't be effective in lowering electric bills unless a customer is being charged for kVA usages. Is this correct?
I don't know of any utility that bills ONLY for kVA use. They are billed for kWH, then their bill is
adjusted for kVA
DEMAND. Demand charges have a time factor in them, usually 15 to 30 minute sliding windows. So as mentioned above, adding a capacitor will have little effect on his demand charges (unless it is one HUGE capacitor?).
And read the above responses more carefully. It will not reduce the
power consumption by any appreciable amount. It only reduces the current on the load side of it. But the kW draw from the utility remains the same. There is an incredibly minute amount of reduction in I
2R losses in the wiring, but in an average facility with properly sized conductors, those losses are so small as to not even be noticeable on a monthly basis. On one installation I investigated for a light commercial customer with about 8,000 sq. ft.of mostly lighting and HVAC loads, I calculated his I
2R savings at roughly $1.20 per year, making his ROI out to about 180 years!
Like I said earlier, these things are scams, or so close to it as to be indistinguishable. They are intended to prey upon the fact that most casual users will not understand the relative complexities of how they pay for energy.