Historically, we have specified power xfmrs that are 55/65 Deg C rated (for U.S. use). My understanding is that this was an older designation used when the insulation was originally transistioned from the older 55 Deg C rating to the newer 65 Deg C rating. My questions are as follows:
1. It seems to me that there is no advantage to specifying a new xfmr as a 55 / 65 deg. C rating. My feeling is that I can simply specify the 65 deg. C rating at the kVA I require and I will end up with what I need. For example, if I needed to serve a 20MVA load, if I specify a 20MVA 65 deg C xfmr I will get the same xfmr as if I had specified a 16.7MVA / 20MVA, 55/65 deg. C xfmr. Does anyone agree or disagree?
2. Is there any economic or technical advantage or disadvantage to specifying the 55/65 rating vs. a 65 rating only?
3. When evaluating xfmr loading on a 55/65 degree rated xfmr per ANSI C57.91, can I simply base my evaluation on the 65 degree C rating using the kVA at 65 deg C?
1. It seems to me that there is no advantage to specifying a new xfmr as a 55 / 65 deg. C rating. My feeling is that I can simply specify the 65 deg. C rating at the kVA I require and I will end up with what I need. For example, if I needed to serve a 20MVA load, if I specify a 20MVA 65 deg C xfmr I will get the same xfmr as if I had specified a 16.7MVA / 20MVA, 55/65 deg. C xfmr. Does anyone agree or disagree?
2. Is there any economic or technical advantage or disadvantage to specifying the 55/65 rating vs. a 65 rating only?
3. When evaluating xfmr loading on a 55/65 degree rated xfmr per ANSI C57.91, can I simply base my evaluation on the 65 degree C rating using the kVA at 65 deg C?