Thanks to all of you, for your great help. you are so kind for having helped me. I have just discovered this web site some days ago, and really it is fantastic.
To be honest with you, I may miss some experience in the heavy industry, so I have been confused by some readings where it was written that kind of things :
SOURCE : WIKIPEDIA
"It is also possible to effect power factor correction with an unloaded synchronous motor connected across the supply. The power factor of the motor is varied by adjusting the field excitation and can be made to behave like a capacitor when over excited."
SOURCE : ABB
"Shunt capacitors, lightly loaded transmission lines and over-excited synchronous machines are capacitive loads and act as sources for reactive power resulting in a leading power factor"
Another source
"At very low power levels the synchronous motor can be made to look capactivie and can be used as a continually adjustable power factor corrector."
Then, with those readings, I mad a misinterpration and I thought that the MVARS produced by an over-excited generator was CAPACITIVE. But, this is not a good way to see the problem.
In fact, I understand now that in overexcitation, the generator will DELIVER VARS instead of consuming (in under-exitation).
So I must then add this VARS to the VARS delivered by the utility, and finally you are right, 13.55 MVARS would be the total MVARS delivered in the case I submitted to you.
Thank a million to all !
Best Regards,
Dan