Power factor measurement.

Status
Not open for further replies.

xchnauzer

Electrical
Joined
Apr 28, 2005
Messages
9
Location
NL
We have two TB5400 units in our facility. Each unit has a meter that displays the power factor and load in MW.
While the load calculations in the facility is done using 0.8pf, I noticed that the pf readings for the two turbines are 0.8 and 0.9 respectively.

Does anyone know why this is?
How do i derive a realistic pf from these readings, if it is possible?
 
Maybe because the generators are running on power factor control with two different settings.

If you are operating in parallel with the grid, the generator power factor can be different than the plant's power factor.

Also, just because load calcs are done using 0.8 pf, I would not assume this has any correlation to the actual power factor.

 
I would imagine the pf fluctuates throughout the day. The 0.8 pf is just for calculating purposes.
 