Suggestions to the previous posting marked by ///\\\:
1) In high voltage capacitors for reactive compensation, why are the insulating transformers used?
///They can trap tripplen harmonics, reduce voltage if needed, isolate zero sequence current, and isolate the capacitors from the grid.\\2) How to calculate the sizing the insulating transformer?
///The rated line current of the capacitor bank + design margin = rated line current of the transformer.\\\
3) What are the other equipment required for the complete package of the capacitor unit for the reactive compensation?
///Discharge resistors, switching equipment to adjust capacitance and thereby compensation, in star connection in-line resistors to reduce inrush currents, safety disconnects, protective devices, and switchgear.\\\
4) How are the other equipment selected?
///According the capacitor banks rated values, and compensation VAR size, compensation steps, capacitors connection, type of capacitors, power quality, etc.\\