I am having a bit of trouble determining what CT burden I will need for a PFC unit which will be connected to a 415V MCC.
I have read a bit of information on the requirements of standard PFC units and from what I can gather they require a Class 1 metering CT and 15 VA burden with 5A secondary.
My question is - can I connect a CT with a greater burden than 15VA? I can only source a 60VA CT due to the size of the busbar it needs to connect to. My thoughts are that it will be ok and that the PFC unit will only draw what current it needs and a burden greater than 15VA will not damage the PFC unit.
Also 1 more question - I have been told to put the CT on the red phase by several sources (manufactures). Why would they recommend this? Surley it doesnt matter what phase the CT is connected to.
Thanks
I am having a bit of trouble determining what CT burden I will need for a PFC unit which will be connected to a 415V MCC.
I have read a bit of information on the requirements of standard PFC units and from what I can gather they require a Class 1 metering CT and 15 VA burden with 5A secondary.
My question is - can I connect a CT with a greater burden than 15VA? I can only source a 60VA CT due to the size of the busbar it needs to connect to. My thoughts are that it will be ok and that the PFC unit will only draw what current it needs and a burden greater than 15VA will not damage the PFC unit.