I agree with waross. According to NEMA MG1 ch.4.20 Grounding Means for Field Wiring recommends
a copper conductor of 1 awg [42 mm^2]. I have to agree with ScottyUK ,also.
In the same paragraph above mentioned in IEC 60034-1, it is stated, however:
"When an earthing terminal is provided in the terminal box, it shall be assumed that the
earthing conductor is made of the same metal as the live conductors.
When an earthing terminal is provided on the frame, the earthing conductor may, by
agreement, be made of another metal (for example, steel). In this case, in designing the
terminal, proper consideration shall be given to the conductivity of the conductor."
If the armor is steel two-tapes made of 0.5 mm thick 90 mm width [iec 60502-1] then the steel total section area will be 90 mm^2.In my opinion, this section correspond only to 15 mm^2 copper, but you need 35.