living2learn
Situation: 12kV switchgear fed from utility. This service entrance switchgear has a 12kV generator connect onto as well as one utility onto the bus and all new SEL-351 relays have been provided for the new incoming generator and utility breakers. All of the existing potential transformers are open delta type and one new wye wye PT was installed on the line side of the generator breaker.
The new generator switchgear is integrating into this one. It has a RTAC to make decisions. This is a closed transition system. The generator has SEL-751A relays and wye wye potential transformers.
The situation...
Looking at the RTAC on my new switchgear we notice a 500V imbalance from the main switchgear. This will still satisfy the sync check relay and etc... but is still concerning. This is looking at the older open delta PT and comparing it to the new wye wye pt that are installed in the same switchgear. The wye wye is on the incoming of the generator and the existing open delta is on the secondary of the utility breaker so it will sync across that breaker. The SEL relays are feeding all the voltage information into the RTAC via IEC 61850 fiber connections. The generator building is 3000' away.
What could cause this 500V imbalance? we have tested the entier system. All older PT's are within .3%, we have added real/reactive load so we know it is capacitance building up...any other thoughts. I read somewhere at sometime that "Thou shall not utilize sync'n with dissimilar PT's" not sure where I read it or if it is applicable with new digital relays now adays.
Client is forcing us to buy new wye wye PT's for his existing switchgear since we cannot confirm where the 500V's is coming from.
IT couldn't be the 30 degree phase shift from the open delta compared to the wye wye because you would think that it would be a much larger.
The situation...