Potential corrosion of the steel rebars within retaining wall 2

Status
Not open for further replies.

dan00

Civil/Environmental
Apr 22, 2005
16
Is it any way to estimate the effective life span of steel reinforcement in a wet environment?
Here is the problem:
The rebars are grouted and located approx 3" or less from the face of the wall.
Where the seepage through retaining wall is occurring, the seepage is through hairline cracks and through grout between blocks. The worst case scenario is to assume that the rebars are in constantly wet condition.
Soil samples of on-site soils adjacent to the wall indicate:
- pH of 8.01
- soluble sulfate content range of 210 to 270 ppm
- chloride content range of 1029 to 1437 ppm
- minimum emectrical resistivity range of 4452 to 5936 ohm-cm.
Thanks a lot
 
Replies continue below

Recommended for you

Roughly 0.13" of thickness lost in twenty years of harsh seashore environment,(each face). The wall described gives good protection to the steel so a lesser loss rate would apply.
 