hokie,
If the calculated extensions were calculated correctly, the different amount of angle change and friction should have been allowed for in the estimated extensions.
hardhatpoke,
Stressing should be done to load/pressure with checks on extension after the stressing is finished to make sure all is ok. It should not be done to an extension. This is a recipe for over stressing and breaking strands. The pressure in the gauge (if it is calibrated correctly) is telling you the force in the strand at the stressing end. The maximum allowed value of this force is an important limit and it is normally the defined stressing force, so overstressing to achieve a calculated extension results in higher forces in the strand than allowed and the possibility that the strand is past yield during the stressing operation. If there were a problem in the duct, such as a slurry blockage, you might only be stressing half the length of the strand and you would end up snapping the strand! This is BAD practice.
We often find that measured extensions on short tendons are high. Never have been able to come up with a definitive reason. If yours are low, you might need to look at the calculated values. Are thhese bonded or unbonded tendons?