1
- #1
JennyNakamura
Structural
- Apr 8, 2011
- 68
Hi Everyone,
I have a large commercial PV project where several hundred solar panels will be installed on the concrete roof of a large industrial building. I knew the contractor would want to use screw anchors, so I spec's Brand A or Brand B because I knew they had ICC approvals. The contractor wants to substitute Brand C but it doesn't have ICC approval, though this screw anchor is very widely used (Redhead LDT). I think this would work fine but I am worried about the ICC issue.
Per the code (IBC 06), Section 1912 says that "...anchors that are not within the scope of App D of ACI 318 [screw anchors in this case]...shall be in accordance with an approved procedure. Section 104.11.1 says "Research reports. Supporting data, where necessary to assist in the approval of materials or assemblies not specifically provided for in this code, shall consist of valid research reports from approved sources." To me this means you gotta have an ICC report, or at least an approval from City of LA, Miami-Dade, State of Florida, etc.
When can I use a post-installed anchor that doesn't have an ICC report? How do others get away with spec'g them -- are they in the wrong?
Thank you in advance....
I have a large commercial PV project where several hundred solar panels will be installed on the concrete roof of a large industrial building. I knew the contractor would want to use screw anchors, so I spec's Brand A or Brand B because I knew they had ICC approvals. The contractor wants to substitute Brand C but it doesn't have ICC approval, though this screw anchor is very widely used (Redhead LDT). I think this would work fine but I am worried about the ICC issue.
Per the code (IBC 06), Section 1912 says that "...anchors that are not within the scope of App D of ACI 318 [screw anchors in this case]...shall be in accordance with an approved procedure. Section 104.11.1 says "Research reports. Supporting data, where necessary to assist in the approval of materials or assemblies not specifically provided for in this code, shall consist of valid research reports from approved sources." To me this means you gotta have an ICC report, or at least an approval from City of LA, Miami-Dade, State of Florida, etc.
When can I use a post-installed anchor that doesn't have an ICC report? How do others get away with spec'g them -- are they in the wrong?
Thank you in advance....