This is regarding anchors for a steel column. The contractor installed the threaded anchor rods at the wrong location. We now have to post-install the rods. I cannot get brand-name epoxy anchor systems to work.
4 - 1" x 24" diameter rods with nut at end
6" spacing each way
I am looking for a creative solution to this problem.
I am considering using a grout with larger diameter cores so I can install the nut into the hole also. Have you used this before? I'm not sure if there will be enough bond. And, I'm concerned that large diameter cores may cause concrete cracking. Imagine trying to create 4 - 2 1/2" diameter x 30" deep cores where the anchors are spaced 6" apart.
Another option is to excavate a 24" square x 30" deep chunk of concrete, reset the rods and reinstate with concrete. But, I'm concerned that failure prism will be affected and hence cause a major reduction in breakout capacity. The new-old concrete interface may not necessarily transfer full rupture capacity thorough the interface due to shrinkage.
What are your thoughts? What do you feel is the better option? Do you have a better solution?